Cable tray support for 9" rung alum cable tray

Cable tray support for 9" rung alum cable tray

distance between supports?
 
How far distance between supports? 2002 code

No requirements in the NEC. Depends on the tray/ladder type the support requirement is tray type and load dependent. Eg. the same tray can be supported with greater interwals for fewer cables. The tray test is for the designated load and a 200# dead load in midspan.

IMO trays should always be supported to their maximum capacity.
 
110.3(B) is what I'd lean towards for proper installation. If it is new tray it should come with documentation, or at least the manufacturer's name to contact for clarification.
 