Cable Tray to EMT Bonding - Separate EGC

Status
Not open for further replies.

Tiki1469

Member
Location
USA
Occupation
Contractor
Job calls for separate bonding conductor because the customer does not want to use the tray as an EGC (24in tray w/ 2 sq.in. cross-section (2000amp). Running separate 3/0 copper or better to bond (3) 1200amp mains to a transformer. They exit the transformer through EMT chase nipples, enter the tray, then enter the 1200amp main enclosures with roughly 2ft EMT nipples. If I understand correctly, I need to bond this cable tray to the EMT on both ends with 3/0 copper or better.

My question is: What is the proper way to bond the tray to EMT? Bonding bushing like rigid?
 
Job calls for separate bonding conductor because the customer does not want to use the tray as an EGC (24in tray w/ 2 sq.in. cross-section (2000amp). Running separate 3/0 copper or better to bond (3) 1200amp mains to a transformer. They exit the transformer through EMT chase nipples, enter the tray, then enter the 1200amp main enclosures with roughly 2ft EMT nipples. If I understand correctly, I need to bond this cable tray to the EMT on both ends with 3/0 copper or better.

My question is: What is the proper way to bond the tray to EMT? Bonding bushing like rigid?
That’s what I would do.
 
Status
Not open for further replies.
Top