Can the vacuum hose pipes be run inside a cable tray carrying low voltage cables with a seperator in between? Please mention the NEC code section ref.
Thanks,
Thanks,
300.8 is not referenced in Article 725. 90.3 permits the rules in Chapter 7 to modify the rules in Chapters 1-4. This is a modification of a Chapter 3 rule.725.3 Other Articles.
Circuits and equipment shall comply with the articles or sections listed in 725.3(A) through (G). Only those sections of Article 300 referenced in this article shall apply to Class 1, Class 2, and Class 3 circuits.