ARTICLE 336 Power and Control Tray Cable: Type TC </font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">I. General</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">336.1 Scope</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">This article covers the use, installation, and construction specifications for power and control tray cable, Type TC.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">336.2 Definition </font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Power and Control Tray Cable, Type TC. A factory assembly of two or more insulated conductors, with or without associated bare or covered grounding conductors, under a nonmetallic jacket.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">II. Installation</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">336.10 Uses Permitted </font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Type TC cable shall be permitted to be used as follows:</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(1) For power, lighting, control, and signal circuits.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(2) In cable trays.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(3) In raceways.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(4) In outdoor locations supported by a messenger wire.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(5) For Class 1 circuits as permitted in Parts II and III of Article 725.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(6) For non?power-limited fire alarm circuits if conductors comply with the requirements of 760.27.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(7) In industrial establishments where the conditions of maintenance and supervision ensure that only qualified persons service the installation, and where the cable is continuously supported and protected against physical damage using mechanical protection, such as struts, angles, or channels, Type TC tray cable that complies with the crush and impact requirements of Type MC cable and is identified for such use with the marking Type TC?ER shall be permitted between a cable tray and the utilization equipment or device. The cable shall be secured at intervals not exceeding 1.8 m (6 ft). Equipment grounding for the utilization equipment shall be provided by an equipment grounding conductor within the cable. In cables containing conductors sized 6 AWG or smaller, the equipment grounding conductor shall be provided within the cable or, at the time of installation, one or more insulated conductors shall be permanently identified as an equipment grounding conductor in accordance with 250.119(B).</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(8) Where installed in wet locations, Type TC cable shall also be resistant to moisture and corrosive agents.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">336.12 Uses Not Permitted </font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(1) Installed where it will be exposed to physical damage</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(2) Installed outside a raceway or cable tray system, except as permitted in 336.10(7)</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(3) Used where exposed to direct rays of the sun, unless identified as sunlight resistant</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(4) Direct buried, unless identified for such use</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">336.24 Bending Radius</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Bends in Type TC cable shall be made so as not to damage the cable. For Type TC cable without metal shielding, the minimum bending radius shall be as follows:</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(1) Four times the overall diameter for cables 25 mm (1 in.) or less in diameter</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(2) Five times the overall diameter for cables larger than 25 mm (1 in.) but not more than 50 mm (2 in.) in diameter</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(3) Six times the overall diameter for cables larger than 50 mm (2 in.) in diameter</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Type TC cables with metallic shielding shall have a minimum bending radius of not less than 12 times the cable overall diameter.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">336.80 Ampacity</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">The ampacity of Type TC tray cable shall be determined in accordance with 392.11 for 14 AWG and larger conductors, in accordance with 402.5 for 18 AWG through 16 AWG conductors where installed in cable tray, and in accordance with 310.15 where installed in a raceway or as messenger supported wiring.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">III. Construction Specifications</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">336.100 Construction </font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">A metallic sheath or armor as defined in 330.116 shall not be permitted either under or over the nonmetallic jacket. Metallic shield(s) shall be permitted over groups of conductors, under the outer jacket, or both.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">336.104 Conductors</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">The insulated conductors of Type TC tray cable shall be in sizes 18 AWG through 1000 kcmil copper and sizes 12 AWG through 1000 kcmil aluminum or copper-clad aluminum. Insulated conductors of sizes 14 AWG and larger copper and sizes 12 AWG and larger aluminum or copper-clad aluminum shall be one of the types listed in Table 310.13 or Table 310.62 that is suitable for branch circuit and feeder circuits or one that is identified for such use.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(A) Fire Alarm Systems Where used for fire alarm systems, conductors shall also be in accordance with 760.27.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(B) Thermocouple Circuits Conductors in Type TC cable used for thermocouple circuits in accordance with Part III of Article 725 shall also be permitted to be any of the materials used for thermocouple extension wire.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">(C) Class 1 Circuit Conductors Insulated conductors of 18 AWG and 16 AWG copper shall also be in accordance with 725.27.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">336.116 Jacket</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">The outer jacket shall be a flame-retardant, nonmetallic material.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">336.120 Marking </font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">There shall be no voltage marking on a Type TC cable employing thermocouple extension wire.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">This is from the 2005 CODE, hope it helps. :)
 