dillon3c

Senior Member
Re: Cable tray

:confused:

Is tray containing electric conductors?

[ May 05, 2005, 05:30 PM: Message edited by: dillon3c ]
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Re: Cable tray

Would placing a divider in the tray to separate the pneumatic lines from any electrical conductors make it OK?

By the way, the pneumatic lines can be installed in a tray with Class 1, 2, and 3 conductors, or Chapter 8 conductors - no divider needed.

Steve

[ May 05, 2005, 11:28 AM: Message edited by: steve66 ]
 

dillon3c

Senior Member
Re: Cable tray

Steve,
can you point me to a specific article # in 725,that quotes this installation/ok ..Haven't located yet,thumbing through the book..
 

dillon3c

Senior Member
Re: Cable tray

I haven't found anything, in support of that statement Steve.From 300-through-Chapter eight as of yet sir..

[ May 05, 2005, 12:06 PM: Message edited by: dillon3c ]
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Re: Cable tray

dillon:

Sure. I had asked the same question about a week ago. See 725.3 - "Only those sections of Article 300 referenced in this article shall apply to Class 1, Class 2 and Class 3 circuits"

So 300.8 - which usually prevents the mixing of electrical with nonelectrical - doesn't apply because it isn't specifically listed anywhere in article 725.

For chapter 8 applications, see 90.3. Same basic principle.

Steve

[ May 05, 2005, 04:05 PM: Message edited by: steve66 ]
 

dillon3c

Senior Member
Re: Cable tray

Steve,
Then I stand corrected, sir..Thank you for the education..Must read somemore on this subject...
 