spurlob6968 Member May 18, 2010 #1 Is it OK to come in to a cable tray with THHN for a splice to the TC cable?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician May 18, 2010 #2 What size is the THHN?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician May 19, 2010 #4 392.8(A) permits splices in the tray. Assuming that your 3/0 is listed for use in cable trap, I don't see an issue.
392.8(A) permits splices in the tray. Assuming that your 3/0 is listed for use in cable trap, I don't see an issue.
eric9822 Senior Member Location Camarillo, CA Occupation Electrical and Instrumentation Tech May 20, 2010 #5 Is it in an industrial establishment with qualified persons maintaining and servicing the installation? 392.3(B)
Is it in an industrial establishment with qualified persons maintaining and servicing the installation? 392.3(B)