NEC 2011 added 300.22 (C) (2) (b) on 'solid side and bottom metal cable tray systems' within other spaces used for environmental air (plenums). As I read this, it appears to now allow the installation of single conductors such as THHN/THWN-2 within a solid enclosed cable tray system (w/ solid top cover) within such 'other type' plenum space, i.e. similar to the allowance for using metal wireways with covers, as it's completely enclosing the wiring method above the ceiling.
I am looking at this installation method for a commercial project, not industrial, above lay in ceiling, large feeder with multiple parallel sets. With existing utilities and a long feeder run, I cannot utilize conduits effectively within the building above the ceiling, and I have to use existing conduits provided in another project by others to get out of main gear (underground) and into the building. Thus my interest in this code change. Comments appreciated, thanks.
I am looking at this installation method for a commercial project, not industrial, above lay in ceiling, large feeder with multiple parallel sets. With existing utilities and a long feeder run, I cannot utilize conduits effectively within the building above the ceiling, and I have to use existing conduits provided in another project by others to get out of main gear (underground) and into the building. Thus my interest in this code change. Comments appreciated, thanks.