cable vs OCPD

Status
Not open for further replies.

rayertz

Member
Location
USA
Can I use 2 sets of 350's to feed a process control panel?

Please see attached sketch.
 

Attachments

  • cable example.pdf
    4.6 KB · Views: 0
Assuming terminations are rated 75 degrees C, I'm pretty sure you need to use 400's to comply with 240.4(B). Or change out that 700A CB and replace with a 600A.
 
I want to use the 350's to the control panel main. I am thinking I can use the OCPD in the control panel to protect the cables upstream.The breaker in the PDP would merely be a switch.
 
If you keep the 700 amp OCPD then your parallel 350's would be tap conductors and the tap rules would apply.
 
Thanks for your help.

I got it worked out with the plant. The original design was to use a 600 amp breaker. If we use a 100% rated breaker they said no problem. So the 700 amp breaker goes away.

Thanks again...
 