Assuming terminations are rated 75 degrees C, I'm pretty sure you need to use 400's to comply with 240.4(B). Or change out that 700A CB and replace with a 600A.
I want to use the 350's to the control panel main. I am thinking I can use the OCPD in the control panel to protect the cables upstream.The breaker in the PDP would merely be a switch.
I got it worked out with the plant. The original design was to use a 600 amp breaker. If we use a 100% rated breaker they said no problem. So the 700 amp breaker goes away.