I need some help on cable sizing as it applies to LV cablebus.
NEC section 370.80 permits the cablebus conductors to be sized based on Table 310.15(B)(17).
Additionally, The NEC handbook (2017) under section 370.80 makes reference to the temperature limitations of the connecting equipment but does not specifically call out section 110.14C. As with all LV equipment (most likely to be terminated with cablebus) you are limited to the 75C ampacity column under table 310.15(B)(16). If the NEC left out section 110.14C on purpose, I am not sure why. It is my opinion to correctly size the cablebus conductors, you would first size the cablebus based on 110.14C (310.15(B)(16)(75C) then utilize Table 310.15(B)(17)(90C) for the conditions of use, selecting the larger of the two cable sizes. This is the same procedure for sizing any other cable application.
I have dealt with cablebus manufacturers over the years and they all stand by utilizing Table 310.15(B)(17) solely for sizing the cablebus conductors and do not take into account 110.14(C). If you take 110.14C into account, then the cable size for cablebus and cable in cable tray would be the same. The only remaining of advantages of cablebus is reduced size as compared to cable in cable tray and a more the robust construction.
NEC section 370.80 permits the cablebus conductors to be sized based on Table 310.15(B)(17).
Additionally, The NEC handbook (2017) under section 370.80 makes reference to the temperature limitations of the connecting equipment but does not specifically call out section 110.14C. As with all LV equipment (most likely to be terminated with cablebus) you are limited to the 75C ampacity column under table 310.15(B)(16). If the NEC left out section 110.14C on purpose, I am not sure why. It is my opinion to correctly size the cablebus conductors, you would first size the cablebus based on 110.14C (310.15(B)(16)(75C) then utilize Table 310.15(B)(17)(90C) for the conditions of use, selecting the larger of the two cable sizes. This is the same procedure for sizing any other cable application.
I have dealt with cablebus manufacturers over the years and they all stand by utilizing Table 310.15(B)(17) solely for sizing the cablebus conductors and do not take into account 110.14(C). If you take 110.14C into account, then the cable size for cablebus and cable in cable tray would be the same. The only remaining of advantages of cablebus is reduced size as compared to cable in cable tray and a more the robust construction.