I am not sure this is the best place to ask this one, thank you for taking the time to look at this.
I am working on a machine in a hazardous location that requires motion. We have e-chains installed along with basket tray.
NEC 300.8 - Installation of conductors with other systems, does not allow other commodities such as pneumatic tubing to run in the same cable tray or raceway as conductors.
I have seen and installed many end effectors that had cables and pneumatics installed in e-chain or other conveyance on the arm. I am looking for anything in the NEC that actually allows this installation method. The machine I am working on is not an arm but does have motion that requires cables and pneumatic hoses to travel with the machine.
Does anyone have any guidance where I might find code that allows this?
I have used fuzzy logic that the term conductor isn't cable therefore doesn't apply to the installation since we are only running cables. I got some sideways looks since we can't find justification in Article 100 definitions to support that notion.
We have separators in the e-chain but they are not continuous.
Thank you for any thoughts on this.
Ken
I am working on a machine in a hazardous location that requires motion. We have e-chains installed along with basket tray.
NEC 300.8 - Installation of conductors with other systems, does not allow other commodities such as pneumatic tubing to run in the same cable tray or raceway as conductors.
I have seen and installed many end effectors that had cables and pneumatics installed in e-chain or other conveyance on the arm. I am looking for anything in the NEC that actually allows this installation method. The machine I am working on is not an arm but does have motion that requires cables and pneumatic hoses to travel with the machine.
Does anyone have any guidance where I might find code that allows this?
I have used fuzzy logic that the term conductor isn't cable therefore doesn't apply to the installation since we are only running cables. I got some sideways looks since we can't find justification in Article 100 definitions to support that notion.
We have separators in the e-chain but they are not continuous.
Thank you for any thoughts on this.
Ken