While being involved in the construction of new sub station I have a habit of hitting all the cad weld connections ( field testing ) with my hammer before buring them with machinery,
problem is these connections have all been tested and approved but I still feel like they need to be physically tested before being buried with heavy equipment !!!!!
There have been a couple that broke loose to my suprise after inspection, they are then repaired and tested again but one would think the cad welds need to take the action of machinery that is placing them into the ground .
If these welds come apart with a little hammer tapping what is going on when a D4 dozer and vibratory roller cover them with 24" of earth and rock?
Anyone with grounding grid systems and cad welding experience your thoughts and ideas will be appreciated.
For what it is worth the welds that I have found as failures have a great looking apperance . have passed the inspectors testing , but the failures have indicated that the cables were not placed centered ( butted against each other) into the cad- weld mold.
These faliures were also on "T" connections only.
problem is these connections have all been tested and approved but I still feel like they need to be physically tested before being buried with heavy equipment !!!!!
There have been a couple that broke loose to my suprise after inspection, they are then repaired and tested again but one would think the cad welds need to take the action of machinery that is placing them into the ground .
If these welds come apart with a little hammer tapping what is going on when a D4 dozer and vibratory roller cover them with 24" of earth and rock?
Anyone with grounding grid systems and cad welding experience your thoughts and ideas will be appreciated.
For what it is worth the welds that I have found as failures have a great looking apperance . have passed the inspectors testing , but the failures have indicated that the cables were not placed centered ( butted against each other) into the cad- weld mold.
These faliures were also on "T" connections only.