knoppdude

Senior Member
Location
Sacramento,ca
Does Cadwelding a grounding electrode conductor violate the code rule that the conductor must be continuous with no splices? I don' have the NEC handy 2008 edition, but if have seen this done to lengthen, and add connections to other grounding electrodes. Thanks for any and all responses.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
From 250.64:

(C) Continuous. Grounding electrode conductor(s) shall be installed in one continuous length without a splice or joint except as permitted in (1) and (2):
(1) Splicing shall be permitted only by irreversible compression-type connectors listed as grounding and bonding equipment or by the exothermic welding process.
 