I'm looking for some opinions, since this really isn't addressed anywhere in code...
In California, as well as some other places, new building are required to install the infrastructure for X number parking spaces with EV charging stations. In my building, it's 20 parking spaces.
I'm in the process of determining what the load and panel space requirements will be. The load I'm using in my calcs is 32A (40A circuit), 208V 1 phase. However, it's possible that what will be installed will be (10) 2-car chargers. Some of those only require a single 32A/40A circuit - i.e., 32A serving 2 parking spots. Obviously that cuts the load in half, as well as the panel space requirement.
If we were actually installing chargers, I could determine what equipment was going in, but since the requirement is merely to provide for possible future chargers, I have 2 different tacks I can take:
1. Install for projected worst case, i.e., (20) 2-pole circuit spaces and a 150 kVA transformer, or
2. Install for a nominal load, (10) 2-pole circuit spaces and a 75 kVA
I am interested to see what other designers have done (or would do).
In California, as well as some other places, new building are required to install the infrastructure for X number parking spaces with EV charging stations. In my building, it's 20 parking spaces.
I'm in the process of determining what the load and panel space requirements will be. The load I'm using in my calcs is 32A (40A circuit), 208V 1 phase. However, it's possible that what will be installed will be (10) 2-car chargers. Some of those only require a single 32A/40A circuit - i.e., 32A serving 2 parking spots. Obviously that cuts the load in half, as well as the panel space requirement.
If we were actually installing chargers, I could determine what equipment was going in, but since the requirement is merely to provide for possible future chargers, I have 2 different tacks I can take:
1. Install for projected worst case, i.e., (20) 2-pole circuit spaces and a 150 kVA transformer, or
2. Install for a nominal load, (10) 2-pole circuit spaces and a 75 kVA
I am interested to see what other designers have done (or would do).