calcuation question need help with

Status
Not open for further replies.

jatindall82

Member
Location
troup, texas
What size branch circuit overcurrent protection device and conductor (THHN) is required for a 19kva of nonlinear loads (75 degree terminals). The branch circuit is supplied by a 208/120v, 4 wire, 3 phase, Wye connected system.

Could someone help me work through this calculation PLEASE!?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
What size branch circuit overcurrent protection device and conductor (THHN) is required for a 19kva of nonlinear loads (75 degree terminals). The branch circuit is supplied by a 208/120v, 4 wire, 3 phase, Wye connected system.

Could someone help me work through this calculation PLEASE!?

How about show us what you have tried. I assume this is homework and we prefer you give it a go first. Also is the load continuous
 

jatindall82

Member
Location
troup, texas
what i have come up with

what i have come up with

I converted the kva to amps

va / (volts x 1.732)
19,000 /(208 x 1.732) = 52.74 amps rounded to 53 amps

branch circuit OCP has to be sized @ 125% of the 53 amps
53 x 1.25 = 66.25 = 66 amps. So a 70 amp OCP

To select the conductor I believe I have to increase 125% also.

66 amps in the 75 degree column requires #4 @ 85 amps

Since there are more than 3 current carrying conductors in the race way I have to correct it.

Do Increase it by 80%???
 