webharvest
I have a situation with a 3phase (208V) system. The panel is total power is 41k and the panel has a 200A main breaker. To calculate the current for the breaker and make sure it meets the 80% rule is the following correct?
I(breaker) = 41k/(208*sqrt(3))= 114A
I was thinking about just using I(breaker)=41k/208 but I think the sqrt(3) comes into play because of the 3phase.
Can you confirm this and maybe give an explanation of the sqrt(3)?