Two 500 kcmils are paralleled. What size copper equipment grounding conductor is needed?
You size the EGC based on the OCPD, which is not given. So I took the 500 kcmil current rating (based on the 75C column) and multiplied by 2 (since they were paralleled). 380x2=760A. This would require an 800 amp OCPD. In 250.122, this equates to a copper EGC of 1/0.
Or do you use the current of 1000 kcmil, which is 545 which would give you a 600 amp OCPD and a 1 AWG EGC?
I believe it's the first one...
You size the EGC based on the OCPD, which is not given. So I took the 500 kcmil current rating (based on the 75C column) and multiplied by 2 (since they were paralleled). 380x2=760A. This would require an 800 amp OCPD. In 250.122, this equates to a copper EGC of 1/0.
Or do you use the current of 1000 kcmil, which is 545 which would give you a 600 amp OCPD and a 1 AWG EGC?
I believe it's the first one...