mstrlucky74
Senior Member
- Location
- NJ
I have a 3P 80A breaker from one panel feeding Panel B right next to it. What would be the correct way to calculate the feeder size? I'm assuming not off the 3P 80a breaker. Should I look at the connected loads of panel B. See attached. Thanks.
I have a 3P 80A breaker from one panel feeding Panel B right next to it. What would be the correct way to calculate the feeder size? I'm assuming not off the 3P 80a breaker. Should I look at the connected loads of panel B. See attached. Thanks.
To allow use of smaller wire if the calculated load on the panel is well below 80A?I don't quite understand why you will feed a 100A panel with an 80A breaker! Am I missing something here?
To allow use of smaller wire if the calculated load on the panel is well below 80A?
Sent from my XT1585 using Tapatalk
And I am saying that if you did not use the smaller breaker you could not use smaller wires. (without invoking tap rules)I'm thinking about the breaker, not the wires.
I don't quite understand why you will feed a 100A panel with an 80A breaker! Am I missing something here?
To allow use of smaller wire if the calculated load on the panel is well below 80A?
Sent from my XT1585 using Tapatalk
I don't recall if 80 amps is a so-called standard size breaker rating or not...
Most commercial style panels are 100 amp minimum so as Digger stated if your calculated load is only 80 amps (or less) then your feeder only needs to be 80 amps. We've installed 100 amp panels with 60 amp feeders.
If you are observant enough, you would see the calculated load (from the load schedule) is above 80 amps. Why choose a breaker with lower rating?:happysad:
Max per phase in load schedule appears to be about 5.6kVA plus the unevaluated existing load on some circuits. Doesn't look like more than 80A to me unless you add the three phase numbers.
Sent from my XT1585 using Tapatalk
IDK how you do things but granting you have 5.6kVA per phase, you should arrive at a line current of 80.89A! We don't choose 80A breaker for that.
The panel schedule lists line to neutral loads.IDK how you do things but granting you have 5.6kVA per phase, you should arrive at a line current of 80.89A! We don't choose 80A breaker for that.