Without knowing the harmonic content of the loads, it is not possible to compute the result. If the 100A load is entirely 3rd harmonic, the load could be 300A on the neutral. If we assume essentially sinusoidal loads, the current on the neutral will be 100A for one phase, 100A for 2 phases, and zero for 3 phases. You need just to do the vector math.
There is a simple mathematical solution only where the loads are linear. With the information give, the calculation is not possible. If the loads were restive the answer would be 100 amps. For that case you can use this formula:I'm sorry, but that is confusing. Given the multiple choice answers (17, 25, 125, or 100 amps), isn't there a simple mathematical solution?
Something like the following:
Step_1: Using Ohm's Law, I(single-phase) = P/E = 12,000 / 120 V = 100 amps per load.
Step_2: Given the loads are lighting, apply the 125% rule; 100 amps x 1.25 = 125 amperes maximum load
Please advise.
If all three lighting loads were turned on at full power at the same time, the current on the neutral would be zero. The maximum neutral current would take place when two of the lighting loads were on full and the third was off. In that case, the current in the neutral would be 100 amps, as others have mentioned already.
The "125% rule" has nothing to do with how much current any given load will draw. Rather, it tells us to select a wire that can handle 125% of the current a continuous load would draw.