There is a 200 amp 1ph service on an old school building.
It consists of a 200 amp overhead riser, 200 amp meter base and a 20 circuit ITE 3r 200 amp main breaker panel mounted on the outside of the building which is full but the school is being used no more and the load on the panel is roughly 60 amps total.
An event took place at the location where the sound guy needed a termination point for a 2/0 cord to run his distribution box for the sound and lighting.
The main in this distribution box is a 150 amp main breaker but doubtful that it pulled that much.
The Electrician at last minute had installed a 3p power distribution block inside the existing panel between the incoming service conductors and the main breaker.
Then installed a 200 amp fused 3r disconnect next to the outdoor panel and extended the service conductors from the PDB to the line side of the 200 a fused disconnect so the sound guy could have a place to terminate the cable.
Is the PDB inside the 1st panel a violation of any sort ? or does this seem to exceed the allowable ampacity of the service conductors?
JAP>
It consists of a 200 amp overhead riser, 200 amp meter base and a 20 circuit ITE 3r 200 amp main breaker panel mounted on the outside of the building which is full but the school is being used no more and the load on the panel is roughly 60 amps total.
An event took place at the location where the sound guy needed a termination point for a 2/0 cord to run his distribution box for the sound and lighting.
The main in this distribution box is a 150 amp main breaker but doubtful that it pulled that much.
The Electrician at last minute had installed a 3p power distribution block inside the existing panel between the incoming service conductors and the main breaker.
Then installed a 200 amp fused 3r disconnect next to the outdoor panel and extended the service conductors from the PDB to the line side of the 200 a fused disconnect so the sound guy could have a place to terminate the cable.
Is the PDB inside the 1st panel a violation of any sort ? or does this seem to exceed the allowable ampacity of the service conductors?