Hello All, I am struggling with some math calculations that seem to contradict each other. I have a retail building that has a 490A connected load. Of the 490A, 360A is continuous and 130A will be non-continuous. See my math below.
[FONT="]Circuit Breaker Sizing[/FONT]
[FONT="]360A X 125% = 450A + 130A @ 100% = 580A[/FONT]
[FONT="] [/FONT]
[FONT="]Conductor Sizing[/FONT]
[FONT="]580A X 125% = 725A = (3) 250MCM = 765A[/FONT]
[FONT="] (2) 500MCM = 760A[/FONT]
By this math, I can use a 600A main service disconnect but when I apply the 80% rule to this thermal magnetic breaker I only have 480A to use. As you can see in my initial explanation, I have a 490A load. Should I just be concerned with the continuous load when applying my calculations? I know in the real world a 600A service will be fine but I am concerned with an inspector applying the 80% rule and saying that the service isn't large enough.
Any help would be appreciated. Thanks
[FONT="]Circuit Breaker Sizing[/FONT]
[FONT="]360A X 125% = 450A + 130A @ 100% = 580A[/FONT]
[FONT="] [/FONT]
[FONT="]Conductor Sizing[/FONT]
[FONT="]580A X 125% = 725A = (3) 250MCM = 765A[/FONT]
[FONT="] (2) 500MCM = 760A[/FONT]
By this math, I can use a 600A main service disconnect but when I apply the 80% rule to this thermal magnetic breaker I only have 480A to use. As you can see in my initial explanation, I have a 490A load. Should I just be concerned with the continuous load when applying my calculations? I know in the real world a 600A service will be fine but I am concerned with an inspector applying the 80% rule and saying that the service isn't large enough.