Is there a justification in the NEC for using measured current load for sizing circuit breakers, conductors, and disconnects, rather than the standard tables and calculations?
For example, let's say we have a machine that contains numerous motors and other devices. Going by the NEC and based on nameplates and datasheets of what is inside, it should hypothetically be sized for 130A disconnects and 2/0 wire. But also hypothetically, according to the recently calibrated and properly functioning meters, it draws less than say 25A RMS under maximum load. Why can't I use a 50A disconnect, 30A breaker, and 10AWG wire?
While erring on the side of safety is good, what happens when I build a factory with scores of similarly overrated machines? I have the power company diverting more resources from the grid to the building, maybe even adding facilities to handle me. I put in huge switchgear. I run fat wire and buy expensive disconnects and breakers, and when I'm done, I'm using a fraction (1/6th) of the current I asked for.
Had it been sized for reality, the power company would not have been involved, the wires and switchgear would be less expensive, and I would say that the plant would still be as safe as can be. Plants do allow for de-rating the overall based on capacity, but each station must be fully rated in most cases.
The people who rated the sub-sub-assemblies erred on the side of caution. The sub-assembly erred further. The whole machine erred further still. Then the plant with 60 or more similarly caution erred stacked machines followed suit, and so did the power company. When several layers each adds 15-25% on top of each other, it gets big in a hurry.
In this hypothetical case, we just spent a lot of money adding infrastructure that is also subject to misfortune. I can make a car almost utterly crash proof, but it will empty your wallet at the gas pump, and crush any other cars on the road, not to mention wear out the roads faster.
My question is, what part of NFPA 70 and 79 allow for measured values of performance to be used in lieu of calculations and table derived results, and what liability is incurred when this route is used? Or must you go strictly by the tables and calculations?
For example, let's say we have a machine that contains numerous motors and other devices. Going by the NEC and based on nameplates and datasheets of what is inside, it should hypothetically be sized for 130A disconnects and 2/0 wire. But also hypothetically, according to the recently calibrated and properly functioning meters, it draws less than say 25A RMS under maximum load. Why can't I use a 50A disconnect, 30A breaker, and 10AWG wire?
While erring on the side of safety is good, what happens when I build a factory with scores of similarly overrated machines? I have the power company diverting more resources from the grid to the building, maybe even adding facilities to handle me. I put in huge switchgear. I run fat wire and buy expensive disconnects and breakers, and when I'm done, I'm using a fraction (1/6th) of the current I asked for.
Had it been sized for reality, the power company would not have been involved, the wires and switchgear would be less expensive, and I would say that the plant would still be as safe as can be. Plants do allow for de-rating the overall based on capacity, but each station must be fully rated in most cases.
The people who rated the sub-sub-assemblies erred on the side of caution. The sub-assembly erred further. The whole machine erred further still. Then the plant with 60 or more similarly caution erred stacked machines followed suit, and so did the power company. When several layers each adds 15-25% on top of each other, it gets big in a hurry.
In this hypothetical case, we just spent a lot of money adding infrastructure that is also subject to misfortune. I can make a car almost utterly crash proof, but it will empty your wallet at the gas pump, and crush any other cars on the road, not to mention wear out the roads faster.
My question is, what part of NFPA 70 and 79 allow for measured values of performance to be used in lieu of calculations and table derived results, and what liability is incurred when this route is used? Or must you go strictly by the tables and calculations?