Hello all. I've got a 12.47kV distribution feeder which is connected to a 3MVA PV site. The protection on the feeder side is a SEL-751. The feeder is grounded wye, and the VT is grounded wye at 60:1.
I didn't create these settings but they "rolled down hill" to me. The 59N function in the SEL-751 is currently set to 12 volts, with zero delay. I would be expecting something more like 80-100 volts secondary. The problem I'm facing is that the folks who set it claim that they simulated faults in the field to generate this setting pickup. I've attempted to explain that this is too low but I'm not gaining much traction. Could someone more experienced in this scheme provide a "rule of thumb" settings value? As mentioned, the delay for the pickup is set to zero, and, not surprisingly, the element is picking up often and tripping the site. I'm pushing the utility to allow us a 20-30 cycle delay here. Any thoughts on that are also most welcome.
And this is my first post, although I've been lurking for over a decade. Thanks in advance!
I didn't create these settings but they "rolled down hill" to me. The 59N function in the SEL-751 is currently set to 12 volts, with zero delay. I would be expecting something more like 80-100 volts secondary. The problem I'm facing is that the folks who set it claim that they simulated faults in the field to generate this setting pickup. I've attempted to explain that this is too low but I'm not gaining much traction. Could someone more experienced in this scheme provide a "rule of thumb" settings value? As mentioned, the delay for the pickup is set to zero, and, not surprisingly, the element is picking up often and tripping the site. I'm pushing the utility to allow us a 20-30 cycle delay here. Any thoughts on that are also most welcome.
And this is my first post, although I've been lurking for over a decade. Thanks in advance!