Our wind turbines experienced abnormal amount of turbine faults and after investigating identified that the faults were caused by high levels of harmonics while the capacitor banks were in service. After harmonic study analysis , identified resonant point at or near 5th harmonics and have high individual harmonic distortion at the 5th , 7th and/or 11th harmonic. So sized and installed a single tuned bandpass filter tuned to 5th harmonic on one of our capacitor bank. See attached for reference.
After installing the filter also, we frequently seen a blown fuses on capacitor banks. So what is the methodology to calculate additional increase in current due to harmonics other than 5th in these capacitor banks , so we can size the fuses and disconnect switches correctly?
Each capacitor bank is 17.5MVAR, rated @34.5KV and we have 4 of them on each bus.