I am trying to calculate the FLA for a motor given the motor kW rating (this is a German motor and they like to give their ratings in kW rather than hp.)but my numbers are not matching up with those given by the manufacturer. I am trying to calculate the FLA as an exercise for myself to try to figure out how to derive them from a given kW.
This is a 480V, 60hz motor rated at 13kW. The motor has a power factor of 75%. I am taking the given 13kW and converting it to a kVA value by dividing it by its power factor of .75. This gives me the following results:
13kW / .75 = 17.3kVA
Then dividing the kVA by the voltage and the factor of 1.73 I get the following:
17.3kVA / .48kV / 1.73 = 20.87A
As you can see the FLA I calculated is 20.87A compared to the 25A that the manufacturer is saying. Did I go about the calculation right for calculating the Amps from a given kW value?
Thanks.
Thanks.