I would like to learn how to do arc flash calculations by hand after using a program to do it. Looking at Equation D.4.2(a) in NFPA 70E 2018 how is the bolted three phase available short-circuit current supposed to be found?
Thanks
In order to calculate the available bolted fault current in your system, you need to get the available fault current from the utility. When you initially ask, a customer service rep will look at a chart and provide you with the bolted fault current based on your transformer size and voltage. This is not what you want as that is based on an infinite bus. You have to be persistent and tell them that it is for arc flash.
Do not use the equations in NFPA 70E-2018 as they are based on IEEE 1584-2002. IEEE 1584-2002 was superseded in November of 2018 by IEEE 1584-2018. This contains new equations based on more testing and will provide a more accurate incident energy value. The downside is that if you are trying to do this by hand, it is very complicated. For example: IEEE 1584-2002 had 3 pages which contained the equations which was 6 equations. IEEE 1584-2018 had 40 pages for the equations and has factors for enclosure size, electrode configuration, etc.
I have attached a page from IEEE 1584-2018 that shows the first equation to calculate the arcing currents. The math is substantial with logs and powers of 6, 5, etc.
View attachment equation.pdf