Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
In the process of labeling disconnects and service equipment for my company at a mine, I noticed no label for available fault current.
Some equations online say to get KVA from transformer and divide by voltage X (1.732 if 3 phase) X Z (impedance)
Others say to Omit z out of equation above use Z as a multiplier to KVA/ volts x 1.732
Z = 100/(Z x plus or minus percent or 0.9)
Therefore the way mike holt showed this is different from the last method
Can I just multiply divisor bottom fraction by impedance shown on transformer name plate? Additionally I’m working on single phase so i won’t be factoring in 1.732. Nor do I know how to factor in service or feeder impedance yet
What is the easiest formula? Thanks
Some equations online say to get KVA from transformer and divide by voltage X (1.732 if 3 phase) X Z (impedance)
Others say to Omit z out of equation above use Z as a multiplier to KVA/ volts x 1.732
Z = 100/(Z x plus or minus percent or 0.9)
Therefore the way mike holt showed this is different from the last method
Can I just multiply divisor bottom fraction by impedance shown on transformer name plate? Additionally I’m working on single phase so i won’t be factoring in 1.732. Nor do I know how to factor in service or feeder impedance yet
What is the easiest formula? Thanks