I searched for this but only came up with an older thread that didn't quite answer my question. I am wondering if "measured along the path of egress" means along a literal line, or over the area(required width along the path).
More context:
We got comments back on a recent permit that we need a photometric map:
I'm using Visual Lighting 2020 to do the luminaire layout and photometric map, and it has the option to do several types of calculation zones, including along a line. Part of me thinks that I should just do a line calculation zone following the egress path, and that will be great. But another part of me thinks it should be a 4ft wide path along that line(or wider if required by occupancy load).
More context:
We got comments back on a recent permit that we need a photometric map:
I went back and studied section 1008.3.5 of the CBC and their comment pretty much sums it up, other than not mentioning the 40:1 rule.Please provide photometric plans to show the emergency lighting to be arranged to provide initial illumination that is at least an average of 1 foot-candle and a minimum at any point of .1 foot-candle measured along the path of egress at floor level.
I'm using Visual Lighting 2020 to do the luminaire layout and photometric map, and it has the option to do several types of calculation zones, including along a line. Part of me thinks that I should just do a line calculation zone following the egress path, and that will be great. But another part of me thinks it should be a 4ft wide path along that line(or wider if required by occupancy load).