Calculating Average Illumination for Path of Egress

cryptonenologist

New User
Location
San Juan Bautista, CA
Occupation
Engineer
I searched for this but only came up with an older thread that didn't quite answer my question. I am wondering if "measured along the path of egress" means along a literal line, or over the area(required width along the path).

More context:

We got comments back on a recent permit that we need a photometric map:
Please provide photometric plans to show the emergency lighting to be arranged to provide initial illumination that is at least an average of 1 foot-candle and a minimum at any point of .1 foot-candle measured along the path of egress at floor level.
I went back and studied section 1008.3.5 of the CBC and their comment pretty much sums it up, other than not mentioning the 40:1 rule.

I'm using Visual Lighting 2020 to do the luminaire layout and photometric map, and it has the option to do several types of calculation zones, including along a line. Part of me thinks that I should just do a line calculation zone following the egress path, and that will be great. But another part of me thinks it should be a 4ft wide path along that line(or wider if required by occupancy load).
 
I searched for this but only came up with an older thread that didn't quite answer my question. I am wondering if "measured along the path of egress" means along a literal line, or over the area(required width along the path).

More context:

We got comments back on a recent permit that we need a photometric map:

I went back and studied section 1008.3.5 of the CBC and their comment pretty much sums it up, other than not mentioning the 40:1 rule.

I'm using Visual Lighting 2020 to do the luminaire layout and photometric map, and it has the option to do several types of calculation zones, including along a line. Part of me thinks that I should just do a line calculation zone following the egress path, and that will be great. But another part of me thinks it should be a 4ft wide path along that line(or wider if required by occupancy load).
You should calculate the entire width of the path.
 