I'm looking at a 120/208V panel schedule that shows the following loading:
Phase A: 12380VA
Phase B: 9586VA
Phase C: 11356VA
Total: 33322VA
So if I look at the total VA of 33322VA does this mean that the panel has a load of 33322/208/1.73 = 92.6A? I would then use this number as the load, and the minimum that the main breaker could be?
If I take any one of the phase let's say phase A and use its load of 12380VA and divide it by the L-N voltage will that give us the current on this phase or 12380/120=103.16A? I'm guessing not since this is over 100A? Cant this be used as an estimation though without considering phase angles?
What if panel wasn't evenly loaded wouldn't you have to look at single phases to verify that no single phase was overloaded? How would you go about this.
So I guess with an evenly loaded panel you always take the total VA added up on all 3 phases and use this total divided by the L-L voltage to come up with the panel load? Is this correct?
Phase A: 12380VA
Phase B: 9586VA
Phase C: 11356VA
Total: 33322VA
So if I look at the total VA of 33322VA does this mean that the panel has a load of 33322/208/1.73 = 92.6A? I would then use this number as the load, and the minimum that the main breaker could be?
If I take any one of the phase let's say phase A and use its load of 12380VA and divide it by the L-N voltage will that give us the current on this phase or 12380/120=103.16A? I'm guessing not since this is over 100A? Cant this be used as an estimation though without considering phase angles?
What if panel wasn't evenly loaded wouldn't you have to look at single phases to verify that no single phase was overloaded? How would you go about this.
So I guess with an evenly loaded panel you always take the total VA added up on all 3 phases and use this total divided by the L-L voltage to come up with the panel load? Is this correct?