Ok, say I have 2000/5 C800 CTs, and I know the bus fault current min/max and what elements are connected to that bus. My question is how do I determine when a CT will saturate, and once I do how do I derive a number for my over current relay?
For example, in a none saturating configuration I would use about a 12 amp definite time pickup because in theory current will always be zero, and 12 amps will cover the minimum bus fault current of 8000 amps.
For example, in a none saturating configuration I would use about a 12 amp definite time pickup because in theory current will always be zero, and 12 amps will cover the minimum bus fault current of 8000 amps.