My local POCO is saying the two situations diagrammed here need different service entrance conductors:
This is PG&E under the Greenbook Section 1.14D:
On the right is a typical residential duplex setup, with solar being back-fed at the bottom of a main panel.On the left is a dedicated back-feed meter.
The left is the setup that exists in my situation.
The POCO says the left requires a 400A service entrance rating, while the right requires just 200A. I can count the numbers in Section 1.14D of the GreenBook and see how they got there. The question is if there is any technical basis for the distinction, or if this is just a lack of consideration of solar in this section?
This is PG&E under the Greenbook Section 1.14D:
On the right is a typical residential duplex setup, with solar being back-fed at the bottom of a main panel.On the left is a dedicated back-feed meter.
The left is the setup that exists in my situation.
The POCO says the left requires a 400A service entrance rating, while the right requires just 200A. I can count the numbers in Section 1.14D of the GreenBook and see how they got there. The question is if there is any technical basis for the distinction, or if this is just a lack of consideration of solar in this section?