Right on, thanks Dennis, I was just curious.
I know there are a few instances where I am calculating the increased egc per 250.122 (B) where the ground increases proportionately with the ungrounded conductors (upsized for vdr). When it's close, I would like to have a way to see if the smaller ground would suffice. For example, if I'm upsizing a (#4 with a #10 grd) to a #1/0 than by calculation (using NEC Table 8) it appears that the ground must be sized to 26,261 or #4 AWG. Seems close enough to a #6, but I would install a #4 ground because 26,261 is larger than 26,240 circular mils.
I know we can calculate the cm by using cm=1000k/ohms per foot. But you still end up just over the #6. The question is, because Table 250.122 includes a range of egc's by ocp, than if I'm at the low end of the range, my judgement wants me to make the call to install the smaller size egc - or at least make an educated decision other than picking a number from a table. However, nothing in the code allows this (to my knowledge). It would seem that if we could somehow calculate the egc, than we could use the calculated size as the basis for increasing for voltage drop.
Anyway, this is probably a moot point, but had my brain turning on this Friday morning. Thanks again.