Hey guys!
I have a background in electrical engineering but am new to the world of electrical design. Would someone be able to explain how the ISC and AIC values are obtained?
Also, in the example I was given, I tried calculating the ISC for the main distribution board. I got ISC=(3000kVA/(480V*1.732))/(5.75%)=62,755 just using the values from the secondary side of the transformer. However, this doesn't seem to match the 49,503A shown on the drawing. Could someone please shed some light on what I am doing wrong?
I've been doing research online but getting really confused. I would be really thankful if you can use my drawing to show some example calculations. Any help is greatly appreciated!
I have a background in electrical engineering but am new to the world of electrical design. Would someone be able to explain how the ISC and AIC values are obtained?
Also, in the example I was given, I tried calculating the ISC for the main distribution board. I got ISC=(3000kVA/(480V*1.732))/(5.75%)=62,755 just using the values from the secondary side of the transformer. However, this doesn't seem to match the 49,503A shown on the drawing. Could someone please shed some light on what I am doing wrong?