Electricalhelp
NJ
I am unable to tell what the wire size is coming from the top, does anyone have any guesses what the incoming service size would be?
How can I get an approximation on the the load from the wire size if the building has abandoned for a few years.
Utility company still has not reach back to me yet.
The wire size size on the bottom is 300 kcmil AL
Is there a service disconnecting means upstream of this enclosure, or perhaps six of them grouped together immediately downstream?
Now, fully admitting my lack of hands-on experience with this, to me it seems strange that six 300's would fit side-by-side at the bottom of that plate. Did I misunderstanding something in your description?
There was no service disconnect or six disconnect downstream. I counted about 10 Panels, some had MCB and others were MLO.
I barely have any hand on experience myself, hence why I was looking for some assistances too.
There are indeed 6 300s on the bottom, if you zoom in you can see the labeling on some of the conductors. That is a big box, probably 3x3 or 4x4. It is kind of hard to tell what is going on there. Almost looks like a "end box" where the power companies conductors attach to the customer's conductors, and the Poco is using more realistically sized conductors like 500 or 750s - however all the conductors go into the same trough which makes me think that is not what is going on. Would help to know where the metering is and a picture of what is to the left.
If you look at my other post about the six disconnect rule, you can find more pics.
But there are (3) 225 AMP Panels, (1) 400 AMP, (1) 200 AMP, (1) 150 AMP, (1) 100 AMP, (3) 30 AMP,