I'm trying to make sure I'm calculating FLA, MCA & MOCP correctly. I've been studying the NEC book and here is my understanding.
For example, a particular warm air furnace has the following:
(2) 10 hp motors, 460/3/60, 10 amps each,
(1) 3 hp motor, 460/3/60, 4.1 amps,
(1) 1.5 hp motor, 460/3/60, 2.5 amps,
control circuit, 115/1/60, 7 amps.
Should FLA @ 460/3/60 be calculated this way?
10 amps + 10 amps + 4.1 amps + 2.5 amps + 1 amp ?
Should MCA be calculated this way?
(10*1.25) + 10 + 4.1 + 2.5 + 1?
Should MOCP be calculated this way?
FLA * 1.75?
Help is appreciated!
Thanks.