I was confused on a question about figuring out the grounding conductor.

It goes something like this, I don't remember the exact question, but its close to this. I just want to know how to approach this type of problem:

If there is an overcurrent device that is rated at 2100A what will the grounding conductor be?
 

Kam1

Member
Location
Chicago, IL
That is not much to go on. Was there any more to the question that you remember?
Minimum size Equipment Grounding Conductors are found in 250.122.


Thanks you.

So if I have to figure out the a grounding conductor and they give me the over current device is 2100A, would I just use the table on 250.122. Size up the conductor and that's how I get the ground or do I go further?

I'm sorry I don't remember the question perfectly this is all that I remember.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Thanks you.

So if I have to figure out the a grounding conductor and they give me the over current device is 2100A, would I just use the table on 250.122. Size up the conductor and that's how I get the ground or do I go further?

I'm sorry I don't remember the question perfectly this is all that I remember.
If the question is that simple then yes. Sometimes the test writers will throw in a little wrinkle or some useless info to trip you up. That is why I asked if there was any more to the question.
 

Kam1

Member
Location
Chicago, IL
If the question is that simple then yes. Sometimes the test writers will throw in a little wrinkle or some useless info to trip you up. That is why I asked if there was any more to the question.

Yes you are correct, I just can't remember what else they were asking. Because I remember I got found that it was 350 kcmil during the test but I didn't know what to do next. Would you know any possible question that could be associated with a question like this? I know its very vague but this is all I remember.
 

hurk27

Senior Member
it will also depend on if the question is asking for the EGC size (250.122) or the GEC size (250.66) 2100 amps sounds like a service and might be a 250.66 question??
Remember bonding conductors ahead of a service is a 250.66 question.


And that is how you get tricked:rant:
 