TheWantonElectrician
Member
- Location
- Madison, WI
- Occupation
- Master Electrician (Residential and small-scale commercial)
I have three questions.
I have a customer building a house approximately 250ft from the existing standalone meter pedestal. The meter pedestal is roughly 250ft from the utility transformer.
I'm trying to determine wire size for the house feeder from that meter.
When doing the calculations:
1) Should I use 250ft or 500ft in my calculations. If it's 500ft, then I will probably try to get the utility to set a transformer closer to the house and run a primary to it and then I'll set the meter on or near the house.
2) should I use 120V or 240v?
3) should I use the panel OC rating (200A), 166A (using 83% rule), or try to calculate the actual house load (presumably <166A)?
I have a customer building a house approximately 250ft from the existing standalone meter pedestal. The meter pedestal is roughly 250ft from the utility transformer.
I'm trying to determine wire size for the house feeder from that meter.
When doing the calculations:
1) Should I use 250ft or 500ft in my calculations. If it's 500ft, then I will probably try to get the utility to set a transformer closer to the house and run a primary to it and then I'll set the meter on or near the house.
2) should I use 120V or 240v?
3) should I use the panel OC rating (200A), 166A (using 83% rule), or try to calculate the actual house load (presumably <166A)?