I've got a medical CT which requires that it's incoming line have an impedance of less than or equal to 105.
The source is approximately 250 feet away and the circuit breaker is required to be 300. I'm not clear if I can use smaller conductors (I suspect I can) but lets assume I use conductors based on the CB and therefore use 350kcmil (rated for 310 under the 75 deg column)
To calculate impedance which table/column should I use in chapter 9 of the NEC.
Table 8 gives ohms per kFT for coated conductors under a subheading of Direct-Current Resistance at 75 deg C. Obviously I have AC current, is this the appropriate column for this application.
If I go to Table 9, here my only options are for "uncoated" copper. Obviously my conductors are insulated, how will that effect my results?
Thanks,
Mike
The source is approximately 250 feet away and the circuit breaker is required to be 300. I'm not clear if I can use smaller conductors (I suspect I can) but lets assume I use conductors based on the CB and therefore use 350kcmil (rated for 310 under the 75 deg column)
To calculate impedance which table/column should I use in chapter 9 of the NEC.
Table 8 gives ohms per kFT for coated conductors under a subheading of Direct-Current Resistance at 75 deg C. Obviously I have AC current, is this the appropriate column for this application.
If I go to Table 9, here my only options are for "uncoated" copper. Obviously my conductors are insulated, how will that effect my results?
Thanks,
Mike