Calculating load for LED strip lighting
olly
Berthoud, Colorado
Master Electrician
If the strip light is 1.46 watts per foot at 12v. Is it as simple as:
1.46 / 12 = . 121A per foot.
So if I were to have 15' it would be
15 x 1.46 = 21.9 watt
21.9 w / 12v = 1.8 A is what this LED strip will draw?
An extra bit of info.
I've looked at the voltage drop on a 2 amp load at 12 volts
Basically, you can go a maximum of 27 feet including the length of the strip if you use 18 gauge wire
Yep. It's straightforward like that
Thanks James. One more follow up. Can I tap off of the microwave circuit? I haven't been able to find in code if the microwave cannot have anything else on it. I would think 1.8A isn't going to cause problems?
Functionally there wouldn't be a problem.
But microwave probably calls for dedicated circuit