Europoljuice
- Florida
- Est. PM
I was reading Charlie's directions and formulas for Calculating a Load on a existing panel. See Below
If you are starting with a new design project, and if you are given a set of loads (in units of amps), some single phase 120, some single phase 208, and some three phase 208, then what you do is,
- Add up all the single phase 120 current values, and mutiply the sum by 120,
- Add up all the single phase 208 current values, and mutiply the sum by 208,
- Add up all the three phase 208 current values, and multiply the sum by 208, and then multiply that result by 1.732,
- Add up the three values calculated above,
- Divide that sum by 208, and divide again by 1.732.
- You now have a design value for the current that will be drawn on each of the three phases (assuming you can balance the loads closely enough). That is the value you use as a design basis for selecting the panel rating, the feeder to the panel, and the feeder breaker from the upstream panel. Be sure to add some margin for future load growth. Most of my clients have asked for 20% above the calculated load.