Hi gang,
I have been tasked with calculating the load on some small 120/240V, 200A panelboards (each one serves equipment at a different cell tower site). A number of the breakers are unlabeled, so I was taking the CB rating x voltage as "worst case".
E.g. 60A/2P breaker is 60Ax240V = 14.4 KVa (7.2 KVa per phase).
My boss (who's a structural) is telling me that the Code says I should be taking 80% of that 14.4 KVa, but I'm not finding that in the Code so far. I have a couple of panels where NOTHING is labeled, so I have no idea of the actual load on each circuit breaker beyond the rating of the breaker.
Can somebody clue me in as to the correct approach and where I can find that in the NEC?
Thanks!