To All:
I have a quick calculation check if anyone is willing. I am scheduling a receptacle panel and want to make sure my thought process is correct.
For the plan, I have a total of 100 receptacles. This is a mix of duplex and quad, and when I change the quads to reflect two duplexs each, I come out to have 117 "duplex" receptacles; 50 continuous load, 67 non-continuous load.
50 x 1.25 x 180VA = 11,250VA (Continuous)
67 x 180VA = 12060VA, but since this is non-continuous over 10,000VA, I have applied a 50% demand factor to everything above 10,000VA. I come up with 11,030VA. (Non-continuous)
Total: 22,280VA.
I am using single-phase 120V, so I then divide 22,280VA / 120V = 185.666A. If I am understanding everything, this will be the total expected load going through my panel.
I am using 20A breakers, which are not supposed to have more than 80% load on them (16A), so I take 185.666A / 16A = 11.6.
So I understand this to mean that I can space roughly 11 receptacles on each 20A circuit breaker and still be ok?
Does any of that make sense to anyone? I am still kinda new to all this. Thanks for taking the time to read and respond.
--Nate
I have a quick calculation check if anyone is willing. I am scheduling a receptacle panel and want to make sure my thought process is correct.
For the plan, I have a total of 100 receptacles. This is a mix of duplex and quad, and when I change the quads to reflect two duplexs each, I come out to have 117 "duplex" receptacles; 50 continuous load, 67 non-continuous load.
50 x 1.25 x 180VA = 11,250VA (Continuous)
67 x 180VA = 12060VA, but since this is non-continuous over 10,000VA, I have applied a 50% demand factor to everything above 10,000VA. I come up with 11,030VA. (Non-continuous)
Total: 22,280VA.
I am using single-phase 120V, so I then divide 22,280VA / 120V = 185.666A. If I am understanding everything, this will be the total expected load going through my panel.
I am using 20A breakers, which are not supposed to have more than 80% load on them (16A), so I take 185.666A / 16A = 11.6.
So I understand this to mean that I can space roughly 11 receptacles on each 20A circuit breaker and still be ok?
Does any of that make sense to anyone? I am still kinda new to all this. Thanks for taking the time to read and respond.
--Nate