While recalculating the electrical loads for a new service on a large commercial property shell only, TI to follow. I noticed that the EEOR sized the entire spaces using the square foot method, for example; future retail space 26,800s.r. x 20w/sq f.t.=52,800w and restaurant loads at 30w/sq ft. = 201,150, etc.
After totaling all of spaces he came up with 4,000,657w @ 4,818 amps thus suggesting that a 5000amp serves would be acquitted.
My question is,
After the total connected loads have been determined using the square foot method, shouldn't you multiply the total by 1.25% therefor the service size should be 6000amp?
If it is necessary to apply the 1.25% to the total Con. load, where in the NEC would it be referenced?
After totaling all of spaces he came up with 4,000,657w @ 4,818 amps thus suggesting that a 5000amp serves would be acquitted.
My question is,
After the total connected loads have been determined using the square foot method, shouldn't you multiply the total by 1.25% therefor the service size should be 6000amp?
If it is necessary to apply the 1.25% to the total Con. load, where in the NEC would it be referenced?