If a calculated load is 99 amps you can install a 100 amp service.
What if your calc came out to 100A? Could you still a 100A service?
What if your calc came out to 100A? Could you still a 100A service?
What I am asking is lets say you have 70 lights with a ballast amp rating of 7amps @ 240volt single phase if you use the ballast amp rating only are you allowed to exceed 80% of the breaker versus ballast amp rating x 1.25 then you can go to 100% of the rating of the main. I am sizing a job for a ballfield and dealing with only light fixture's.
What I am asking is lets say you have 70 lights with a ballast amp rating of 7amps @ 240volt single phase if you use the ballast amp rating only are you allowed to exceed 80% of the breaker versus ballast amp rating x 1.25 then you can go to 100% of the rating of the main. I am sizing a job for a ballfield and dealing with only light fixture's.
In that case 220.3 (b) (1)and then 220.22
What I am asking is lets say you have 70 lights with a ballast amp rating of 7amps @ 240volt single phase if you use the ballast amp rating only are you allowed to exceed 80% of the breaker versus ballast amp rating x 1.25 then you can go to 100% of the rating of the main. I am sizing a job for a ballfield and dealing with only light fixture's.
What I am asking is lets say you have 70 lights with a ballast amp rating of 7amps @ 240volt single phase if you use the ballast amp rating only are you allowed to exceed 80% of the breaker versus ballast amp rating x 1.25 then you can go to 100% of the rating of the main. I am sizing a job for a ballfield and dealing with only light fixture's.
In that case 220.3 (b) (1)and then 220.22
Are those 08 references?
Are those 08 references?
NO. I know 02' by heart (pretty much)
We're on 05' I don't own on 08'
that's an 02' article.
NO. I know 02' by heart (pretty much)
We're on 05' I don't own on 08'
that's an 02' article.
Okay. I am 05 also. I will look up the references using the cross reference chart in the back.
Okay. I am 05 also. I will look up the references using the cross reference chart in the back.
I'll save you some time,it says
An outlet for a specific load shall be computed based on the ampere rating of the load served.
basiclly what rob said
I'll save you some time,it says
An outlet for a specific load shall be computed based on the ampere rating of the load served.
basiclly what rob said
Gotcha. Thanks.
What if your calc came out to 100A? Could you still a 100A service?
IMO if your NEC load calculation finishes at 100.00 amps you may install a 100 amp service with a typical 100 amp breaker.
70x7x240x1.25= service size