If a calculated load is 99 amps you can install a 100 amp service.
What if your calc came out to 100A? Could you still a 100A service?
What I am asking is lets say you have 70 lights with a ballast amp rating of 7amps @ 240volt single phase if you use the ballast amp rating only are you allowed to exceed 80% of the breaker versus ballast amp rating x 1.25 then you can go to 100% of the rating of the main. I am sizing a job for a ballfield and dealing with only light fixture's.
In that case 220.3 (b) (1)and then 220.22
Are those 08 references?
NO. I know 02' by heart (pretty much)
We're on 05' I don't own on 08'
that's an 02' article.
Okay. I am 05 also. I will look up the references using the cross reference chart in the back.
I'll save you some time,it says
An outlet for a specific load shall be computed based on the ampere rating of the load served.
Gotcha. Thanks.
IMO if your NEC load calculation finishes at 100.00 amps you may install a 100 amp service with a typical 100 amp breaker.
70x7x240x1.25= service size