JFletcher
Senior Member
- Location
- Williamsburg, VA
With residential loads, most times cost would be (watts x hours)/1000 x kw/hr electrical cost. However, I was trying to figure out the cost of heating water, say for a hot shower or bath. Would this be a matter of converting BTU to kw/hr? I've worked out the following:
Gallons of water x 8.34 lbs/gal = lbs of water
a BTU is raising one pound of water 1*F
Total lbs of water x temperature change (ΔT) = Total BTU
1kW-hr = 3412 BTU, or 1 BTU = 0.29W-hr
So, say you take a shower that uses 10 gallons of hot water @ 120*F. Water coming into the water heater is, say, 60*F. Assume a kW-hr of electricity costs $0.12.
10gal x 8.34lbs/gal x 60 = 500.4 BTU
500.4 BTU x 0.29 W-hr = 145 W-hrs = .145 kW-hrs x $0.12 kW-hrs = $0.02 per shower?
This seems very low. I know I'm not compensating for pressure nor heat loss through pipes, but still, where is my math off?
This would be the equivalent of sticking a 150W flood bulb into a thermally insulated 10gal pail of 60* water and that pail being 120* in an hour.
Gallons of water x 8.34 lbs/gal = lbs of water
a BTU is raising one pound of water 1*F
Total lbs of water x temperature change (ΔT) = Total BTU
1kW-hr = 3412 BTU, or 1 BTU = 0.29W-hr
So, say you take a shower that uses 10 gallons of hot water @ 120*F. Water coming into the water heater is, say, 60*F. Assume a kW-hr of electricity costs $0.12.
10gal x 8.34lbs/gal x 60 = 500.4 BTU
500.4 BTU x 0.29 W-hr = 145 W-hrs = .145 kW-hrs x $0.12 kW-hrs = $0.02 per shower?
This seems very low. I know I'm not compensating for pressure nor heat loss through pipes, but still, where is my math off?
This would be the equivalent of sticking a 150W flood bulb into a thermally insulated 10gal pail of 60* water and that pail being 120* in an hour.