I'm doing a loose look at a temporary service in which I have a 150 Kva and a 300 Kva XFMR both 480V feeds. I need to put the circuits in a panel schedule but not sure how much Kw to carry for them. The amps off the chart seem high.
150kVA is ~180A @ 480/277V; 300kVA is about 360A.I'm doing a loose look at a temporary service in which I have a 150 Kva and a 300 Kva XFMR both 480V feeds. I need to put the circuits in a panel schedule but not sure how much Kw to carry for them. The amps off the chart seem high.
Spot on.150kVA is ~180A @ 480/277V; 300kVA is about 360A.
I was thinking he meant MV to 480/277V.Since you did not say I am guessing that the transformers are 480 V primary and 208-120 secondary.
Why would you run 480 to a construction trailer?I was thinking he meant MV to 480/277V.
I mean, it's a really nice construction trailer though.Why would you run 480 to a construction trailer?
I have no idea, but 300kVA and 150kVA at 208/120V is about 1250A total; that seems like a lot of current for a construction trailer. But I don't work in construction, so I dunno about that, either.Why would you run 480 to a construction trailer?