Calculating the Size of Pull-Box Needed

Status
Not open for further replies.
We are doing the electrical on a mixed use, multi family project in Marina del Rey, CA.

Scenario:

My superintendent and I are attempting to size pull-boxes correctly for the unit subfeeds. We have MC cable feeders running from the group metering, located in the parking deck, to pull boxes, and then transitioning at the pull-boxes to SER cable that will be run up through the concrete podium deck and through the wood structure portion of the project, and then to the unit panels.

We have looked through the NEC, but can't seem to locate this scenario for sizing the pull boxes. I only see sizing based on conduit size entering the pull boxes, not MC cable or SER. Also, how do we factor for all the splices we will have in those pull boxes? Each splice will be an insulated Polaris connector.

Thanks for the help.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I would size it base on the KO that is used for the cables. I am not sure that is correct but that is what I would do.
 

cpinetree

Senior Member
Location
SW Florida
Along with Dennis' answer you might make up your joints in the shop and then measure the space needed.

Using the dimensions of the connectors required to terminate MC and SER you likely will have a box that is tight to work in with the polaris taps.
 
Thanks everyone for your responses.

I think you are all correct, in that I should just transpose the required KO size for the cable, into conduit size. The 314.28 code reference makes sense, and I think applies to our situation.

What do you guys think about all the splices in the pull-box? Increase by about 25%? I really don't think the code will speak on this portion. I also doubt that an inspector could gig us, as long as we size it to the minimum required by NEC, and then increase it some for the Polaris splices.
 
Along with Dennis' answer you might make up your joints in the shop and then measure the space needed.

Using the dimensions of the connectors required to terminate MC and SER you likely will have a box that is tight to work in with the polaris taps.

Good idea. That would give us an idea of how much space they will really take up.
 

kwired

Electron manager
Location
NE Nebraska
Is that really the same? 4-500's in an MC cable with a 2" connector will not fit in a 2" raceway.
I will second that, needs to transpose to same raceway size one would use for the conductors involved, they pack them into a tighter space in a cable assembly then what code lets you put into a raceway.

And if you are going to splice them code minimum sized box isn't always going to be large enough, you find that out the hard way sometimes.
 
I will second that, needs to transpose to same raceway size one would use for the conductors involved, they pack them into a tighter space in a cable assembly then what code lets you put into a raceway.

And if you are going to splice them code minimum sized box isn't always going to be large enough, you find that out the hard way sometimes.

Hmmm. Ok, so the general consensus is to size the box based on the required EMT raceway size for the conductors being used. We will have a range of conductor sizes, from 1/0, up through 4/0 (3C with Ground). If we plan on just sizing the box for all 4/0 conductors (2.5" KO size) entering/exiting, that should give us plenty of space to work with the Polaris splices.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Hmmm. Ok, so the general consensus is to size the box based on the required EMT raceway size for the conductors being used. We will have a range of conductor sizes, from 1/0, up through 4/0 (3C with Ground). If we plan on just sizing the box for all 4/0 conductors (2.5" KO size) entering/exiting, that should give us plenty of space to work with the Polaris splices.

Logically that would make sense since with raceways the pull box is sized according to the trade size of the raceway so an equivalent size for cables would allow the same amount of room.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I agree also. The cable connector does not have to follow a 40% fill-- my bad too.....Calculate the size of the raceway that would be needed for those conductors and then use that size.
 