I need to power (3) chiller banks
Each bank has the following electrical characteristics:
208V 3Phase
RLA = 677
MCA = 691
MOP = 700
I think these are continuous loads. Here's my calculation:
(3)(677)*1.25= 2539 amps
Does this mean I would need a 3000 amp distribution panel with 3000 amp fuses?
I don't even know if RLA is the same as FLA. I've always thought that FLA is 0.8*MCA. If we take (691)(0.8) it's 552.8 amps which is not even close to the RLA.