Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
Ive been away from studying NEC code for a while but I wanted to get back into it.
I came across article 110.6 when trying to determine wire size in Kcmil for stranded conductors, the circular mill area for each strand must be multiplied by the number of strands to determine the circular mill area of the conductor.
If i remember correctly if 6 awg or larger is installed in conduit, it must be stranded
Also how is this sizing applied for stranded wire in general? If chapter 9 table 8 says 250 kcmil is 37 (quantity) is this quantity strands since strand numbers are not given elsewhere?
Then 250,000 mil x 37 strand (quantity) = 9,250,000 mills total
This doesnt make sence
A 14 AWG is 4110 mils for both 1 and 7 quantity, so is this done?
I came across article 110.6 when trying to determine wire size in Kcmil for stranded conductors, the circular mill area for each strand must be multiplied by the number of strands to determine the circular mill area of the conductor.
If i remember correctly if 6 awg or larger is installed in conduit, it must be stranded
Also how is this sizing applied for stranded wire in general? If chapter 9 table 8 says 250 kcmil is 37 (quantity) is this quantity strands since strand numbers are not given elsewhere?
Then 250,000 mil x 37 strand (quantity) = 9,250,000 mills total
This doesnt make sence
A 14 AWG is 4110 mils for both 1 and 7 quantity, so is this done?