Theoretically, if you have a 120/240 Delta supply and load it to 10 amps on L1/L3 and 20 amps on L2/L3 (nothing between L1/L2), what would the amperage be on the L3 conductor (I'm assuming L1 will have a 10-amp load and L2 will have a 20 amp load)?

My understanding is you take the common current (10-amps) and multiply by 0.866 then add in the difference in the currents which is 10-amps. The would be 8.66+10 for 18.66 amps on L3.

I've been told I'm incorrect. What is wrong with my thinking?
 
The current on L3 would be √ ( 102 + 202 + 10 x 20 ) = 26.46A

Using this formula with equal 20A L-L loads across L1/L3 and L2/L3 we have:
√ ( 202 + 202 + 20 x 20 ) = √ ( 3 x 202 ) = √3 x 20 = 1.732 x 20 = 34.64A which is the familiar result for balanced currents.
 
The current on L3 would be √ ( 102 + 202 + 10 x 20 ) = 26.46A

Using this formula with equal 20A L-L loads across L1/L3 and L2/L3 we have:
√ ( 202 + 202 + 20 x 20 ) = √ ( 3 x 202 ) = √3 x 20 = 1.732 x 20 = 34.64A which is the familiar result for balanced currents.
Ok. That is now in a SS.
Now what is the formula for unbalanced loads of 5, 10, 15?
 
For a delta with terminals A, B, and C, let IA, IB, and IC be their respective line currents.
Let IAB be the L-L load current on A and B, IBC the current on B and C, and IAC the current on A and C.

Then:
IA = √ ( IAB2 + IAC2 + IAB + IAC )
IB = √ (IAB2 + IBC2 + IAB x IBC )
IC = √ ( IAC2 + IBC2 + IAC x IBC )


Now what is the formula for unbalanced loads of 5, 10, 15?

For IAB = 5, IBC = 10, IAC = 15 :

IA = √ ( 52 + 152 + 5 x 15 ) = 18.0
IB = √ ( 52 + 102 + 5 x 10 ) = 13.2
IC = √ (152 + 102 + 15 x 10 ) = 21.8
 
Last edited:
For a delta with terminals A, B, and C, let IA, IB, and IC be their respective line currents.
Let IAB be the L-L load current on A and B, IBC the current on B and C, and IAC the current on A and C.

Then:
IA = √ ( IAB2 + IAC2 + IAB + IAC )
IB = √ (IAB2 + IBC2 + IAB x IBC )
IC = √ ( IAC2 + IBC2 + IAC x IBC )

It is worth noting that this assumes that the line currents IA, IB, and IC are pairwise 120 degrees out of phase (for a consistent sense of positive.) I.e. all the loads are resistive, or they all have the same leading or lagging power factor.

(Also, the IA formula has an obvious typo, the last plus sign should be a times sign.)

Cheers, Wayne
 
It is worth noting that this assumes that the line currents IA, IB, and IC are pairwise 120 degrees out of phase (for a consistent sense of positive.) I.e. all the loads are resistive, or they all have the same leading or lagging power factor.
Typo in the above, I meant the load currents IAB, IBC, and ICA, as my subsequent comment implies.

Cheers, Wayne
 
In complex I23=20*[cos(-120)+sin(-120)i ];I31=10*[cos(-240)+sin(-240)i]

I12=0; I23=-10-17.32i; I31=-5+8.6603i

So, I1=I12-I31=5-8.66i; I2=I23-I12=-10-17.32; I3=I31-I23 I3=-5+8.66i+10+17.32i=5+25.98i

I3=sqrt(5^2+25.98^2)=26.457
 