Calculating Vd of 120/208 V circuit

Status
Not open for further replies.

unsaint33

Member
Location
Minnesota
when calculating the max voltage drop of 3% for feeder (or branch circuit) for a 120/208V, do I want the Vd to be 3% of 120V or 208V? And does that change for the 5% of the total circuit?
 
Last edited:

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
So, in order to select the feeder conductors big enough to limit the Vd under 3%, should my 3% Vd be 3.6V or 6.24V? (3.6V is 3% of 120V & 6.24V is 3% of 208V)
If you have 3% VD on the L-N side, that would be 116.4 V. That would make the L-L voltage 201.6 V, or a 3% VD.


if the feeder has the same current on all three legs, the VD will be the same L-L as L-N.

I should have said the VD in % is the same. Obviously the voltage drop in volts is not the same.
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
So, in order to select the feeder conductors big enough to limit the Vd under 3%, should my 3% Vd be 3.6V or 6.24V? (3.6V is 3% of 120V & 6.24V is 3% of 208V)

They are all telling you straight.
3% Voltage drop on each 120V leg gets you 3% Voltage drop on the phase to phase 208V

It is a vector (trigonometry) problem. Vphase-neutral X sqrt(3) = Vphase-phase
120V X 1.732 = 207.8V

Works the same for the Voltage Drops
3% X 120V = 3.6V
3.6V X 1.732 = 6.24V

.03 X 207.8V = 6.23V

The only difference we are seeing is the round off error.

The attached sketches show the angles.
 

Attachments

  • 208-120.pdf
    54.3 KB · Views: 0
  • 208-120 VD.pdf
    66.3 KB · Views: 0

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
They are all telling you straight.
3% Voltage drop on each 120V leg gets you 3% Voltage drop on the phase to phase 208V

It is a vector (trigonometry) problem. Vphase-neutral X sqrt(3) = Vphase-phase
120V X 1.732 = 207.8V

Works the same for the Voltage Drops
3% X 120V = 3.6V
3.6V X 1.732 = 6.24V

.03 X 207.8V = 6.23V

The only difference we are seeing is the round off error.

The attached sketches show the angles.

I deal with balanced lines (3 phase PV inverters), so for me the answer is simple; it's just the one way drop on an individual conductor @120V. There's no current on the neutral, so no voltage drop.
 